Grounding-type receptacles are installed downstream of a GFCI on a circuit that has no equipment grounding conductor. How must they be marked?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7009
- D: GFCI Protected and No Equipment Ground
Explanation
Under 406.4(D)(2)(c) (406.12(D) in NEC 2026), grounding-type receptacles supplied through a GFCI may replace nongrounding ones, but each must be marked GFCI Protected and No Equipment Ground. No equipment grounding conductor may be connected between these receptacles.