What is the maximum setting of an instantaneous trip breaker for a squirrel cage motor other than Design B energy efficient?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8014
- D: 800 percent of full-load current
Explanation
Table 430.52 allows instantaneous trip breakers up to 800 percent of the table full-load current for these motors. Design B energy efficient motors may go to 1100 percent. Instantaneous trip breakers must be adjustable and part of a listed combination controller.