Question 8015 of 731 · Texas Journeyman Electrician Exam
The calculated motor short-circuit protection value does not match a standard size. What does 430.52 permit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8015
- A: The next higher standard size
Explanation
Exception No. 1 to 430.52(C)(1) permits the next higher standard rating from 240.6 when the percentage in Table 430.52 does not correspond to a standard size.
More questions: Motors, HVAC, Generators and Transformers