Question 8033 of 931 · Texas Journeyman Electrician Exam
A motor is connected wye-start, delta-run. Conductors between the controller and the motor are selected at what portion of the full-load current?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8033
- D: 58 percent of the motor full-load current
Explanation
Section 430.22(C) bases the conductors between controller and motor in a wye-start, delta-run connection on 58 percent of the motor full-load current. Each set of windings carries only part of the line current.
More questions: Motors, HVAC, Generators and Transformers
- 8034Feeder conductors supplying several motors must have an ampacity of at least what?
- 8035A feeder supplies three motors with table FLCs of 40 A, 20 A and 10 A. What is the minimum feeder conductor ampacity?
- 8036How is the maximum feeder short-circuit and ground-fault protective device for a motor feeder determined?
- 8037The largest motor on a feeder has a 100 A branch-circuit breaker. The other motors have FLCs of 20 A and 10 A. What is the maximum standard feeder breaker size?
- 8038When may several motors be connected to a single branch circuit?
- 8039Which nameplate value is used to size branch-circuit conductors for a packaged air conditioning unit?