Question 8036 of 731 · Texas Journeyman Electrician Exam
How is the maximum feeder short-circuit and ground-fault protective device for a motor feeder determined?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8036
- C: The largest branch-circuit device rating plus the sum of FLCs of the other motors
Explanation
Section 430.62(A) limits the feeder device to the largest rating of any branch-circuit short-circuit and ground-fault device in the group plus the sum of the full-load currents of the other motors. Unlike branch circuits, the feeder rule does not allow rounding up.