A rooftop HVAC unit requires a service receptacle. What is the maximum distance from the equipment?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8043
- D: 25 ft
Explanation
Section 210.63 requires a 125 volt, single-phase, 15 or 20 ampere receptacle outlet for servicing heating, air conditioning and refrigeration equipment. It must be readily accessible and within 25 ft of the equipment.
More questions: Motors, HVAC, Generators and Transformers
- 8044What other location rule applies to the HVAC service receptacle?
- 8045May the HVAC service receptacle be connected to the load side of the equipment disconnecting means?
- 8046Branch-circuit conductors for a single hermetic motor-compressor must have an ampacity of at least what?
- 8047What is the normal maximum branch-circuit short-circuit protection for a single hermetic motor-compressor?
- 8048A single-phase cord-and-plug connected room air conditioner needs what protection device in or on the cord?
- 8049A room air conditioner is the only load on a 20 ampere individual branch circuit. What is its maximum marked rating?