Question 8045 of 731 · Texas Journeyman Electrician Exam
May the HVAC service receptacle be connected to the load side of the equipment disconnecting means?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8045
- B: No, it may not be on the load side of the equipment disconnect
Explanation
Section 210.63 prohibits connecting the service receptacle to the load side of the equipment disconnecting means. Otherwise the receptacle would be dead whenever the unit is switched off for service.
More questions: Motors, HVAC, Generators and Transformers
- 8046Branch-circuit conductors for a single hermetic motor-compressor must have an ampacity of at least what?
- 8047What is the normal maximum branch-circuit short-circuit protection for a single hermetic motor-compressor?
- 8048A single-phase cord-and-plug connected room air conditioner needs what protection device in or on the cord?
- 8049A room air conditioner is the only load on a 20 ampere individual branch circuit. What is its maximum marked rating?
- 8050A room air conditioner shares a branch circuit with lighting outlets. What is its maximum rating?
- 8052Conductors from generator terminals to the first overcurrent device must have an ampacity of at least what?