What is the normal maximum branch-circuit short-circuit protection for a single hermetic motor-compressor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8047
- B: 175 percent of rated-load current, up to 225 percent if needed to start
Explanation
Section 440.22(A) limits the device to 175 percent of the rated-load current or branch-circuit selection current. If that will not carry the starting current, it may be increased up to 225 percent.