Question 8048 of 731 · Texas Journeyman Electrician Exam
A single-phase cord-and-plug connected room air conditioner needs what protection device in or on the cord?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8048
- C: A leakage-current detector-interrupter (LCDI) or an AFCI
Explanation
Section 440.65 requires single-phase cord-and-plug connected room air conditioners to have a factory-installed LCDI or AFCI. It detects cord damage and opens the circuit before a fire starts.
More questions: Motors, HVAC, Generators and Transformers
- 8049A room air conditioner is the only load on a 20 ampere individual branch circuit. What is its maximum marked rating?
- 8050A room air conditioner shares a branch circuit with lighting outlets. What is its maximum rating?
- 8052Conductors from generator terminals to the first overcurrent device must have an ampacity of at least what?
- 8053A 20 kW, 240 volt single-phase generator supplies a distribution panel. What is the minimum ampacity of the conductors from the generator terminals to the first overcurrent device?
- 8057Within how many seconds must an emergency system provide power after loss of normal supply?
- 8058Within how many seconds must a legally required standby system provide power after loss of normal supply?