Question 8039 of 731 · Texas Journeyman Electrician Exam
Which nameplate value is used to size branch-circuit conductors for a packaged air conditioning unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8039
- B: Minimum circuit ampacity (MCA)
Explanation
Equipment with hermetic motor-compressors is marked with a minimum circuit ampacity under 440.4(B), and the conductors must be at least that value. The MCA already includes the 125 percent factor for the largest motor.
More questions: Motors, HVAC, Generators and Transformers
- 8040An air conditioning unit nameplate shows a maximum overcurrent protection (MOCP) of 40 A. What breaker is permitted?
- 8041Where must the disconnecting means for an outdoor air conditioning condenser be located?
- 8043A rooftop HVAC unit requires a service receptacle. What is the maximum distance from the equipment?
- 8044What other location rule applies to the HVAC service receptacle?
- 8045May the HVAC service receptacle be connected to the load side of the equipment disconnecting means?
- 8046Branch-circuit conductors for a single hermetic motor-compressor must have an ampacity of at least what?