Question 8051 of 931 · Texas Journeyman Electrician Exam
What is the minimum ampere rating of the disconnecting means for a hermetic motor-compressor rated 1000 volts or less?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8051
- B: 115 percent of rated-load or branch-circuit selection current, whichever is greater
Explanation
Section 440.12(A)(1) requires the disconnect to have an ampere rating of at least 115 percent of the nameplate rated-load current or branch-circuit selection current, whichever is greater. A horsepower rating is also required, based on the rated-load and locked-rotor currents.
More questions: Motors, HVAC, Generators and Transformers
- 8052Conductors from generator terminals to the first overcurrent device must have an ampacity of at least what?
- 8053A 20 kW, 240 volt single-phase generator supplies a distribution panel. What is the minimum ampacity of the conductors from the generator terminals to the first overcurrent device?
- 8054What must a generator other than a cord-and-plug connected portable generator be equipped with?
- 8055Which receptacles on a portable generator rated 15 kW or smaller must have GFCI protection?
- 8056A permanently installed optional standby generator supplies a home. What must prevent it from feeding back into the utility system?
- 8057Within how many seconds must an emergency system provide power after loss of normal supply?