What must a generator other than a cord-and-plug connected portable generator be equipped with?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8054
- A: A lockable disconnect that separates the generator from the circuits it supplies
Explanation
Section 445.18 requires generators to have one or more disconnecting means that simultaneously open all ungrounded conductors and can be locked in the open position. Workers can then isolate the generator from the premises wiring.
More questions: Motors, HVAC, Generators and Transformers
- 8057Within how many seconds must an emergency system provide power after loss of normal supply?
- 8058Within how many seconds must a legally required standby system provide power after loss of normal supply?
- 8059An optional standby system uses an automatic transfer switch and no load management. What capacity must the system have?
- 8061A transformer rated 1000 volts or less has primary protection only, and the primary current is 9 A or more. What is the maximum primary overcurrent device rating?
- 8062A small control transformer has a primary current of 5 A and primary protection only. What is the maximum primary overcurrent device rating?
- 8063A transformer with primary-only protection has a rated primary current below 2 A. What is the maximum primary overcurrent device rating?