A transformer is located out of sight of its supply disconnect. What does 450.14 require?

Exactly one answer is correct.

Show solution

Correct answer to question 8071

  • D: The disconnect must be lockable open, and its location must be marked on the transformer

Explanation

Section 450.14 requires a disconnecting means for transformers other than Class 2 and Class 3 types, located in sight of the transformer or at a remote location. A remote disconnect must be lockable in the open position (110.25) and its location must be field marked on the transformer.