125-volt, 15- and 20-ampere receptacles installed in elevator pits, hoistways, and on car tops require what protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10007
- A: GFCI protection for personnel
Explanation
Article 620 requires GFCI protection for 125-volt, single-phase, 15- and 20-ampere receptacles in pits, hoistways, on car tops, and in machinery spaces. These areas can be damp and are worked in by maintenance personnel.