Question 10075 of 931 · Texas Journeyman Electrician Exam
An EVSE capable of bidirectional power flow that is used as an optional standby or interactive source must meet which requirement?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10075
- A: It must be listed for the purpose and installed per the relevant power source articles
Explanation
EVSE that exports power from the vehicle to premises wiring must be listed and marked for that function, and the installation must comply with Articles 702, 705, or 706 as applicable. Proper listing ensures safe interconnection.
More questions: Special Equipment, Pools, PV and EV
- 10076The OCPD for a fire pump motor must be sized to carry what current indefinitely?
- 10078Under NEC 2026, fire pump supply and control conductors inside a building protected by concrete encasement require at least how much concrete?
- 10083A transformer arc welder has a rated primary current of 50 amperes and a 50 percent duty cycle. The I1eff value is not marked. Using a duty cycle multiplier of 0.71, what is the minimum supply conductor ampacity?
- 10084The OCPD for an arc welder may be rated at not more than what percentage of the rated primary current (I1max)?
- 10085For a feeder supplying a group of arc welders, what percentage is applied to the two largest welders' current?
- 10001Each commercial building and occupancy accessible to pedestrians must have at least one outlet for sign or outline lighting at each tenant entrance. What branch circuit must supply it?