Using the NEC 2026 standard method, what is the demand load for one 16 kW range?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12019
- C: 9.6 kW
Explanation
Above 12 kW, Column C is increased 5 % for each kW over 12 (Table 120.55, Note 1). 16 kW is 4 kW over, so 8 kW x 1.20 = 9.6 kW.
More questions: Load Calculations