In the NEC 2026 optional method for a single dwelling, how is a 9,600 VA EVSE treated?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12036
- D: Added at 100 % of its load
Explanation
120.82(D) requires the EVSE load from 120.57 to be included at 100 %, outside the general loads that receive the 8 kVA / 40 % treatment. For a 9,600 VA charger that means the full 9,600 VA is added.
More questions: Load Calculations