Under the NEC 2026, what load is included for each 2-wire small-appliance branch circuit in a dwelling unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12041
- A: 1,500 VA
Explanation
120.52(A) assigns 1,500 VA to each 2-wire small-appliance circuit, and 120.52(B) assigns at least 1,500 VA to each laundry circuit. Both may be combined with general lighting before the demand factors are applied.
More questions: Load Calculations