Under the NEC 2026, what is the calculated load for 8 household electric dryers rated 6,000 W each on one feeder?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12045
- A: 28,800 VA
Explanation
Each dryer counts at 6,000 VA, so 8 x 6,000 = 48,000 VA (120.54). The demand factor for 8 dryers is 60 %. 48,000 VA x 0.6 = 28,800 VA.