Question 12046 of 731 · Texas Journeyman Electrician Exam
Under the NEC 2026, what is the calculated load for 30 household electric dryers rated 5,000 W each on one feeder?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12046
- B: 47,250 VA
Explanation
Each dryer counts at 5,000 VA, so 30 x 5,000 = 150,000 VA (120.54). For 24 to 42 dryers the factor is 35 % minus 0.5 % per dryer above 23: 35 - 3.5 = 31.5 %. 150,000 VA x 0.315 = 47,250 VA.
More questions: Load Calculations
- 12047Under the NEC 2026, what is the calculated load for 2 household electric dryers rated 5,000 W each on one feeder?
- 12048Under the NEC 2026, what is the calculated load for 45 household electric dryers rated 5,000 W each on one feeder?
- 12056Which dwelling load contributes nothing to the neutral in an NEC 2026 feeder calculation?
- 12058A 10-unit apartment building has 1,000 ft2 units, each with two small-appliance circuits and one laundry circuit. What is the NEC 2026 standard method demand for lighting, small-appliance and laundry loads on the service?
- 12001Using the standard method under the NEC 2026, what general lighting load must be included in the service calculation for a one-family dwelling with 2,400 ft2 of livable floor area?
- 12002A 2,000 ft2 dwelling has the minimum two small-appliance circuits and one laundry circuit. Under the NEC 2026 standard method, what is the demand load for general lighting, small-appliance and laundry loads combined?