Question 12040 of 731 · Texas Journeyman Electrician Exam
Which statement about the 2 VA per ft2 dwelling unit load in the NEC 2026 is correct?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12040
- D: It is used for service and feeder calcs only
Explanation
120.41 uses 2 VA per ft2 for dwelling service and feeder calculations. The number of general lighting branch circuits is still based on 3 VA per ft2 (120.13), and small-appliance and laundry circuits are added separately at 1,500 VA each (120.52).