NEC 2026 optional method: 2,200 ft2 dwelling, two small-appliance and one laundry circuit, 12 kW range, 5 kW dryer, 1,200 VA dishwasher, 900 VA disposal, 4.5 kW water heater, 5,000 VA AC (larger than heat) and a 9,600 VA EVSE. What is the total calculated load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12038
- B: 32,400 VA
Explanation
General loads = 32,500 VA; 8,000 VA + 40 % of 24,500 VA = 17,800 VA (120.82(B)). Add AC at 100 % (5,000 VA, 120.82(C)) and the EVSE at 100 % (9,600 VA, 120.82(D)) for 32,400 VA.
More questions: Load Calculations