NEC 2026 standard method: a dwelling has a 1,200 VA dishwasher, 900 VA disposal, 4,500 W water heater and a 7,680 VA EVSE. What is the combined load for these four items?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12037
- A: 14,280 VA
Explanation
EVSE is excluded from the 75 % fastened-in-place appliance rule (120.53), so only three appliances remain and they count at 100 %: 6,600 VA. The EVSE adds its nameplate 7,680 VA (120.57), total 14,280 VA.