A 48 A continuous EVSE operates at 240 V. What load does it add to an NEC 2026 dwelling service load calculation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12035
- C: 11,520 VA
Explanation
The load is the nameplate value, 48 A x 240 V = 11,520 VA (120.57). 120.5(E) states that the 125 % continuous load factor is not part of the load calculation; it is applied later when sizing the branch circuit conductors and OCPD.