NEC 2026 standard method: 2,800 ft2 dwelling, two small-appliance and one laundry circuit, 1,200 VA dishwasher, 800 VA disposal, 4,500 W water heater, 1,100 VA microwave, 12 kW range, 5 kW dryer, 10 kW heat (larger than AC) and an EVSE with no nameplate data. What is the calculated load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12042
- B: 41,385 VA
Explanation
Lighting 5,600 VA + 4,500 VA = 10,100 VA, demand 5,485 VA; four appliances 7,600 VA x 75 % = 5,700 VA; range 8,000; dryer 5,000; heat 10,000; EVSE 7,200 VA (120.57, not in the 75 % group). Total 41,385 VA.