The informational note for feeder conductor sizing recommends that feeder voltage drop not exceed what percentage?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3052
- A: 3 percent
Explanation
The informational note suggests feeders sized to limit voltage drop to 3 percent, with feeders and branch circuits together not exceeding 5 percent. Informational notes are not enforceable requirements.