Question 8069 of 931 · Texas Journeyman Electrician Exam

A 150 kVA dry-type transformer rated over 112.5 kVA is installed indoors. Generally, where must it be installed?

Exactly one answer is correct.

Show solution

Correct answer to question 8069

  • A: In a transformer room of fire-resistant construction

Explanation

Section 450.21(B) requires indoor dry-type transformers over 112.5 kVA to be installed in a transformer room of fire-resistant construction, with exceptions such as transformers with high-temperature insulation separated by barriers or distance.

Next to question ›