When the 120 percent rule is used for a load-side interconnection, where must the backfed breaker be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10059
- D: At the opposite end of the busbar from the main supply OCPD
Explanation
The 120 percent allowance requires the PV backfed breaker to be positioned at the end of the busbar opposite the primary supply. This prevents any part of the busbar from carrying more than its rating.