Question 12017 of 731 · Texas Journeyman Electrician Exam
Standard method (NEC 2026): the only fastened-in-place appliances are a 1,200 VA dishwasher, a 900 VA disposal and a 5,000 W water heater. What appliance load goes into the calculation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12017
- A: 7,100 VA
Explanation
The 75 % demand factor applies only to four or more fastened-in-place appliances (120.53). With three appliances the full 7,100 VA is used.
More questions: Load Calculations
- 12033Under the NEC 2026 load calculation rules, an EVSE in a dwelling has no nameplate rating available. What load is used for it?
- 12034A 24 A, 240 V EVSE with a nameplate rating of 5,760 VA is added to a one-family dwelling. What EVSE load is used in an NEC 2026 standard method calculation?
- 12035A 48 A continuous EVSE operates at 240 V. What load does it add to an NEC 2026 dwelling service load calculation?
- 12036In the NEC 2026 optional method for a single dwelling, how is a 9,600 VA EVSE treated?
- 12037NEC 2026 standard method: a dwelling has a 1,200 VA dishwasher, 900 VA disposal, 4,500 W water heater and a 7,680 VA EVSE. What is the combined load for these four items?
- 12038NEC 2026 optional method: 2,200 ft2 dwelling, two small-appliance and one laundry circuit, 12 kW range, 5 kW dryer, 1,200 VA dishwasher, 900 VA disposal, 4.5 kW water heater, 5,000 VA AC (larger than heat) and a 9,600 VA EVSE. What is the total calculated load?