Question 8042 of 931 · Texas Journeyman Electrician Exam
Is a disconnect permitted on or within an air conditioning unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8042
- C: Yes, but not on panels designed for access or where it covers the nameplate
Explanation
Section 440.14 permits the disconnect to be installed on or within the equipment. It must not be located on panels designed to allow access to the equipment and must not obscure the nameplate.
More questions: Motors, HVAC, Generators and Transformers
- 8043A rooftop HVAC unit requires a service receptacle. What is the maximum distance from the equipment?
- 8044What other location rule applies to the HVAC service receptacle?
- 8045May the HVAC service receptacle be connected to the load side of the equipment disconnecting means?
- 8046Branch-circuit conductors for a single hermetic motor-compressor must have an ampacity of at least what?
- 8047What is the normal maximum branch-circuit short-circuit protection for a single hermetic motor-compressor?
- 8048A single-phase cord-and-plug connected room air conditioner needs what protection device in or on the cord?