Under the NEC 2026, a feeder supplies a 40 A continuous load and no noncontinuous load. Which pair of values is correct?

Exactly one answer is correct.

Show solution

Correct answer to question 12039

  • C: Load calc 40 A, conductor at least 50 A

Explanation

120.5(E) keeps the 125 % factor out of the load calculation, so the calculated load is 40 A. When the feeder conductors and OCPD are sized (215.2, 215.3), the continuous load is still taken at 125 %: 40 x 1.25 = 50 A.